Forum discussion

NC-2009 IEQp1:Minimum indoor air quality performance

Single Zone Ventilation Calculation

We have a project which has an big roof top lounge served by RTU, the same unit serve adjacent corridor & storages so this is basically an single zone system with no VAV terminal boxes, so while updating IAQ performance calculator for single zone we are allowed to enter just the RTU naming and not all the spaces served by the system. How do to deal with this situation?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 07/31/2018 - 12:02

Boggarm, while you do not have a system with multiple thermal zones, you do have a system with multiple ventilation zones. You should use the multi-zone method.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.