NC-2009 IEQp1:Minimum indoor air quality performance

A single big space which include several functions.

Hi All, I'm now working on a project under LEED NC certification. The ground floor includes a conference room, offices, technical spaces, meeting rooms, and one big space, in which the following functions are located without any physical separations: - Two lobbies with reception desk - Corridors and circulation - Break area - Cafeteria The above-mentioned big space is served by 2 AHUs (which serve also other rooms). We pursue the verification according to ASHRAE 62.1:2007 and I'd like to understand which kind of space use we have to verify for this big space. Can we separate in different singles functional units, even if these are not physically separated? Thanks.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 11/02/2015 - 13:54

I would separate it into different spaces based on use. Upload a floor plan showing how the spaces are separated and what the area of each space is.