Service water heating for process water usage

I have a commercial kitchen facility that has a number of plumbing fixtures used for pot filling, etc, which are considered process water (and is reflected as such in the Water Use Reduction calculations).  Since these fixtures utilize hot water, can the energy used to heat this process water also be considered part of the process load?  This would have to be separated from the energy used to heat other plumbing fixtures (lavatories, hand sinks, etc).

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 04/26/2018 - 20:09

Process water use does not always translate to process energy use. Service hot water use like you describe is not a process load on the energy side since 90.1 regulates this energy use. So the energy use for hot water associated with this purpose does not need to be separated.