FAQs about EAp2 :

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

Semiheated Walls

I've interpreted the semiheated column in table 5.5-1 refering to the external walls of a semiheated space...as this table is much conserned with the envelope (the partition between the semiheated space and the heated space being irrelevant as it does not lay on the envelope. It could, however, be interpreted as being the wall (partition) between the semiheated space and the conditioned space where if the semiheated space has external facing walls they will require the values of either the nonresidential or residential columns. This case is unconventional to me because the film co-eff. on either side of the semiheated partition are not really standardized and therefore the U-values don't make so much sence. What is the correct interpretation.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 03/07/2013 - 15:17

Refer to 5.5.2 and figure 5.5. To us it appears to be both the external walls and internal partitions to a conditioned space of a semi-heated space must meet the semi-heated column requirements. The one that bugs me is the partition between conditioned and unconditioned but not ventilated space as only requiring the semi-heated levels of insulation.

Thu, 03/07/2013 - 15:57

Thanks Markus. As it happens my figure is very badly visible in my eddition...I can't make out much. Maybe the logic is something like "two semiheated makes a whole".

Fri, 03/08/2013 - 19:52

Wow. Check out A9.4.1.1 and A9.4.1.2. It seems the second option is indeed the correct one. I would have called it a semi-exterior "partition".

Sat, 04/13/2013 - 19:23

Just a update after deeper investigation... Semiheated baseline requirements Semiheated spaces are defined in ASHRAE as spaces having cooling capacities less than 5 Btu/h•ft2 and have heating capacities that range from 3.4 Btu/h•ft2 up to the values in Table 3.1 (5 Btu/h•ft2 for climate zones 1 and 2, 10 Btu/h•ft2 for climate zone 3, 15 Btu/h•ft2 for climate zones 4 and 5, 20 Btu/h•ft2 for climate zones 6 and 7, and 25 Btu/h•ft2 for climate zone 8). Exterior surfaces for semiheated spaces should be modeled in the Baseline Case using the semi-conditioned values from Tables 5.5-1 to 5.5-8. Semi-exterior baseline requirements ASHRAE defines semi-exterior building envelope as: “The elements of a building that separate conditioned space from unconditioned space or that enclose semiheated spaces through which thermal energy may be transferred to or from the exterior, or to or from unconditioned spaces, or to or from conditioned spaces.” For example, a slab separating an unconditioned parking garage from the conditioned first floor of a building would be considered a semi-exterior element. Similarly, a wall separating a semiheated warehouse from a conditioned office space would be considered a semi-exterior element. As per the User's Guide, semi-exterior surface constructions should be modeled so as to adhere to the semiheated criteria from Tables 5.5-1 to 5.5-8 (even though they may not have anything to do with a semiheated space). However, one cannot use the same constructions for a semi-exterior wall of a semiheated space as that of the exterior wall of a semiheated space. The Max. Assembly U-Values listed in these tables under the semiheated criteria were calculated using the exterior air film R-Value co-efficients listed in section A9.4.1 NOT those of semi-exterior "partitions". This means that semi-exterior surfaces must adhere to the same criteria as the exterior surface, but due to the differing applicable air film resistances, should use different constructions to come to the required U-value. Lastly, as per the User's Manual, other interior partitions shall have the same build as those of the proposed design.

Thu, 04/18/2013 - 11:23

On a side note: external floors rated U-values are indeed calculated with an external air film resistance as that of a semi-exterior surface (probably because the underside doesn't experience the same wind as that of a roof or wall), meaning that in this case the semi-exterior surface floor element construction happens to be identical to that of the semiheated floor (for appendix G).

Add new comment