Does this credit require the use of Section 11, or can Appendix G be used? I previously asked this about EAc1.3, but this credit does state section 11 in the language. Any input would be appreciated.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 03/11/2014 - 18:43

Section 11 can be used to demonstrate 90.1 compliance. Appendix G cannot be used to demonstrate 90.1 compliance. This prerequisite requirement is related to 90.1 compliance. EAc1.3 is not about compliance but is about relative improvement. So for the prerequisite you must meet the prescriptive requirements or follow the performance path (section 11), for the credit you can use either modeling methodology.