Michael, Our local regulations usually require rainwater collection facilities that only shift the total runoff between storms instead of infiltrating or reusing the rainwater. Is there a common accepted definition of runoff quantity that in relation to the time period (during the rainstorm OR during and after the rainstorm)? Thank you.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 10/27/2015 - 02:01

I'm sorry I don't think I understand your question.

Wed, 10/28/2015 - 00:49

Let me reformulate the question: A zero lot line building with no rainwater infiltration or reuse pursues case 2 for SSc6.1 by storing the rainwater on a tank and releasing the rainwater into the city's sewers gradually after the rainstorm. If we define runoff as "runoff during the storm", the runoff would be: total rainwater - tank's capacity If we define runoff as "runoff during and after the storm", the runoff would be total rainwater.

Wed, 10/28/2015 - 11:32

You do not meet. You need to reduce quantity (volume) by 25%. You may be reducing "rate" with your approach but the volume is the same.