FAQs about EAp2 :

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

View answers »

Forum discussion

NC-2009 EAp2:Minimum Energy Performance

Residential Lighting

Hi Marcus, it seems that this is a real issue in this forum and I ended up more confused.

Help me get this thing right

First, lets clarify some basic concepts:

According to the Energy Star Multifamily High Rise Program Simulation Guidelines, section 3.6, GENERAL LIGHTING energy savings may be claimed as long as the proposed design complies with lighting requirements. Then, section 3.6.2 IN-UNIT LIGHTING states that if hardwired lighting is specified, the actual LPD must be modeled and does not specify if they must meet illumination requirements. However, while filling the Energy Star Calculator, it comes to my attention that there is a column for illumination levels, but doesn't interferes with the Proposed LPD output the calculator gives me to input into my model.

This makes me think two things.

1.- Is General Lighting all the luminaries fixtures installed outside the dwelling units, and only these have to meet lighting requirements in order to claim savings?

2.- Is In-unit lighting all the luminaries fixtures installed inside the dwelling units, and as long as they are hardwired, you can claim savings and model the actual proposed LPD even though they might not comply with illumination requirements in some rooms?

This is very important for a project we are about to submit to review, since all this time we thought that we would not be able to claim energy savings for in-unit lighting, and we were claiming savings for outside lighting. Our approach was to use Building Area Method for the whole building in both models (0.70 w/sf) and Exterior according to ASHRAE Table 9.4.5 Tradable Exterior Lighting. Thanks in advance!

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 04/06/2018 - 17:06

1. Lighting outside the dwelling units is regulated by 90.1 and is covered by that standard and not the Simulation Guidelines you cite. 2. No. You must demonstrate that the hardwired lighting meets the illumination requirements in the Guideline for spaces inside dwelling units.

Fri, 04/06/2018 - 17:38

Thank you for the quick answer! 

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.