I found a thread from 2011 discussing the Addendas released 5/9/11 removing the footnote that was previously changed under Addenda reliease 9/19/10. Can someone set me straight if i'm not interpreting the 5/9/11 addenda correctly? I interpret the new requirement as: Case 1) If I have a system that serves only 1 space that is densely occupied, the only requriement of this credit is a CO2 sensor. An OA measurement device is not required. Case 2) System that serves 20% or more non-densely occupied spaces, and has one densely occupied conference room. I will need to provide a CO2 sensor for the Conference room AND an OA measurement device on the system, since i'm serving 20% or more densely occupied spaces. Thanks!
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium for
Andrew Mitchell, P.E.
PrincipalMitchell Gulledge Engineering, Inc.
LEEDuser Expert
126 thumbs up
October 18, 2012 - 10:40 am
Barbara, you are correct for both cases. Just one note; remember that the 20% refers to 20% of the supply airflow serving non-densely occupied spaces. It does not refer to 20% of the floor area.