The prerequisite compliance should either be a calculation of the ventilation rates (as shown in IEQp1 Tables 1, 2 and 3 of the LEED Reference Guide) or it should be a table stating compliance with the prescriptive requirements of ASHRAE 62.1 Section 5.1 (as shown in IEQp1 Table 4). Your quoted text seems over the top for the Prerequisite; perhaps is it a review comment for an attempt at IEQc2 using natural ventilation?
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
I think Amanda is correct. I am dealing with the same text also. 62.1-2007 section 4 is about this measurement and I have not found a reason for exclusion. Of course, the outdoor air should be good, but organizing a detailed measurement for this requirement is a load on the budget.
Does anyone have experience in this one? On what ruling should I know that it is not needed?
Gerrit-Jan, can you clarify your question?Where are you seeing the text Amanda quotes as a required upload for IEQp1?
Add new comment
To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.