FAQs about EAp2 :

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

Renovation Project (Envelope Question)

The reviewer has asked us for the existing envelope conditions prior to retrofit to be modeled consistent with the requirements of ASHRAE 90.1-2007 Table G3.1.5(Baseline)(f) which says " For existing building envelopes, the baseline building design shall reflect existing conditions prior to any revisions that are part of the scope of work being evaluated." However, since the project before retrofit included more glazing area than the new proposed design, it is unclear if the baseline and the proposed glazing percentage can DIFFER. Please note the same Table G3.1.5 (Baseline) at the beginning, explicitly says" Equivalent dimensions shall be assumed for each exterior envelope component type as in the proposed design". If following this last statement, the breakdown of new, renovated and existing parts in both alternative becomes excruciating. Additionally if glazing in both alternatives is the same, will the new wall area replacing part of the glazing in the proposed project need to be compared to and Ashrae 90.1 envelope baseline value instead to the existing? Thanks

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 10/07/2015 - 14:27

This is somewhat of a grey area. One provision says that the glass area has to be the same (up to 40%) and the other says you can model the existing conditions. There is a conflict so which should prevail? In my opinion the glazing area in the baseline should be identical to the proposed. That should prevail. It is the fairest comparison.If you closed in some windows I think it is legitimate to get some credit for it. You then model the baseline envelop with the existing U-value and R-value. We did a project a few years ago that had no windows in the existing building. The project created windows all over. It certainly not make sense to compare a windowless baseline to the proposed with windows. I think the same logic applies the other way too.

Wed, 10/07/2015 - 14:42

Thanks Marcus, Like you said, it would make sense for them to restrict window percentage up to 40% when the existing building does not have windows and now you are proposing windows, but the other way around, can we argue a bit of credit by reducing window sizes? Right now I have: BASELINE (Existing): 21% glazing 79% wall Proposed: 14.5% new glazing 15.2% new wall 70% existing wall to remain Also these percentages are matching the architects numbers under MRc1.1

Wed, 10/07/2015 - 15:23

That makes sense to me. You should be able to get some credit for closing in windows.