CI-2009 IEQp1:Minimum IAQ Performance

Renovated spaces or whole building for ASHRAE 62.1

Hello, We have a project that consists of renovating 3 separate spaces in a large commercial building. The building was designed under ASHRAE 62.1-1999 (applicable standard at the time) and received a LEED silver rating. When complying with IEQp1 we understand that the ventilation systems serving the spaces to be renovated must comply with ASHRAE 62.1-2007. Is it also required to provide new ventilation air calculations under 62.1-2007 for rest of building as well?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 11/14/2013 - 13:45

Matt, ASHRAE 62.1-2007 compliance is only required for the spaces within the proposed LEED-CI scope. That said, any adjustments made, could impact other spaces in the building, especially if you have multi-zone VAV systems.