NC-2009 IEQp1:Minimum indoor air quality performance

regularly occupied zones

Do we need to include spaces such as corridors, store rooms when computing the outdoor air requirement using the 62MZCalc ? Or do we include only regularly occupied zones in the calculation? Please advice.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 01/07/2015 - 09:35

Good morning, you have to consider all occupied spaces, and you can exclude inactive space. Thanks for your attention, LEEDme

Wed, 01/07/2015 - 09:40

Hi, thank you. so do you mean that i can cosider storage rooms & corridors as inactive spaces?

Wed, 01/07/2015 - 10:42

Dear Stella, You can find answer at IEQ space matrix http://www.usgbc.org/resources/eq-space-type-matrix . Storage rooms without permanent working places are considered unoccupied. Egress stairway or dedicated emergency exit corridor are considered unoccupied, otherwise it must be ventilated according to table 6-1 of AHRAE 62.1.