We have a hospital project using varable water cooled screw chiller with the minimum COP of 5.9 which is defined as per Path B ASHRAE 90.1 2013
Now as per ASHRAE 90.1 2013, we have to follow Path A for chiller efficiency in basecase where COP comes around 6.11.
So, the proposed case chiller COP(5.9) is less than basecase chiller COP(6.11). Am i making any mistake in selecting the baseline path?
Thanks in advance.