FAQs about EAp2 :

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

Refrigerations system

Do the refrigeration system such as walk-in coolers or refrigeration cases must be detailed modeled in the simulation program (E+)? or is it possible consider them as a process loads?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 06/28/2013 - 14:20

They are a process load. How you calculate or model the energy use is up to you. You should do so as accurately as you can within reason. If they are a significant part of the overall energy use more time should be taken to ensure accuracy. The greater the impact on overall usage the more time should be spent.

Wed, 07/24/2013 - 08:02

About the process load in Retail, the table 1 of EAc.1 have to be used for both baseline and proposed? In case we have a detailed datasheets of process equipments, may we use these values both for baseline and proposed in place of table 1? Thank you

Wed, 07/24/2013 - 13:31

The table which lists the values for a variety of retail equipment should be used for the Baseline. You should model the Proposed with the actual equipment being installed. Hopefully your Proposed systems use less energy than the Baseline!

Fri, 07/26/2013 - 14:21

But, if in the table 1 the characteristics of the machines are very different (or even missing) respect those that we have in the Retail (the location is in Italy and there are specific mechanical process of food preparation), how do we have to do? Do we have to use the same values of the Proposed also in the Baseline? Thank you very much

Fri, 07/26/2013 - 14:39

The purpose of table 1 was to establish baselines that projects could claim savings against. If you are not claiming any savings simply model the proposed equipment identical in the baseline.