Hello,

I have a doubt regarding the need to ventilate refrigerated warehouses or storage rooms.

As per Addenda L of ASHRAE 62.1 - 2010, refrigerated strorage rooms with a cooling setpoint below 50ºF need to be ventilated. However, LEED interpretation #10423 states that it is not required to ventilate refrigerated storage rooms with a setpoint of 32ºF (0ºC) or lower.

There is also a doubt regarding the space's type as some of them may qualify as "Inactive Storages" as per definition 4 of IEQ Space Matrix.

 

1) Is it necessary to ventilated a refrigerated storage room below 32ºF (0ºC)?

2) There are 2 types of refrigerated rooms: refrigerated storage rooms used for storage purposes only (occupancy occurs daily, less than 15 min at a time and for retrieval purposes) and refrigerated rooms intended for both storaging purposes and for human activity (may be occupied for more than 15 min at a time for a given person). May any of these types be excluded from ventilation? My opinion is that only those inteded for human activity should be ventilated.

Thanks in advance!
 

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 03/20/2019 - 15:36

Hi Luis, I think that LEED Interpretation takes precedence over ASHRAE's addenda. If your cold storage area cannot be adjusted from below 32 °F (0 °C) to above 32 °F (0 °C), and if no combustion equipment (such as gas-operated forklifts) is operated in the space, you don't have to ventilate the cold room.   Regards,

Thu, 03/21/2019 - 11:53

We have successfully used ASHRAE 62.1-2013 since it includes rooms kept below 50 degrees F (10 degrees C). this has no area based or people based requirement, so if the space is unoccupied then ventilation is not required.   