FAQs about EAp2 :

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

reference systems for a warehouse building

We are working on a warehouse project with small attached administration building. I have a question regarding reference systems for this project. The warehouse building has floor heating and exhaust fans (outdoor air is supplied naturally via loading gates; there's no cooling system). Administration building (which is smaller than 1900sqm) has a separate HVAC system (AHUs and VRF system). 1. According to table G3.1.1A the reference system for the warehouse (predominant condition) should be system 7. However there are no supply fans in the proposed case so I'm not sure if we should include them in the reference model? 2. Since the administration office is smaller than 1900sqm exception a) of section G3.1.1 doesn't apply. In that case since there are different occupancy and loads schedules than in the warehouse we assumed that exception b) should be implemented and system 4 should be modeled (electric heating in the administartion building), is that correct?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 09/09/2014 - 14:09

To avoid some of the "rules" around heating only systems I would apply Addendum dn and model the warehouse as a system 9 or 10. Then apply exception b to the office.

Thu, 09/11/2014 - 10:43

Thank you Marcus. I checked Addendum dn and as you mentioned system 11 would be most appropriate for the warehouse. If I understood it well, this system should be modeled as packaged rooftop with warm air furnance? And I have one more question regarding fans in this reference system: 1. In the proposed case there are only exhaust fans (outdoor air is supplied naturally via loading gates). Should the fans in the reference be simulated identically as in the proposed case or should the energy usage of the reference fans be calculated based on ASHRAE guidelines (power of fans calculated based on pressure drop only for exhaust airflow control devices)?

Thu, 09/11/2014 - 14:52

The addendum mislabels the system numbers. If you look in 90.1-2010 they are labeled system 9 and 10. ASHRAE 90.1-2010 defines System Type 9 as a constant volume warm air furnace, gas fired, with no cooling. System Type 10 is defined as a constant volume warm air furnace, electric resistance. The Baseline efficiencies for these systems should be determined based on ASHRAE 90.1-2007 Table 6.8.1E. Baseline system air flow rates for System Types 9 and 10 shall be determined based on the temperature differential between 105 degrees F and the design space heating temperature setpoint, the minimum outdoor air flow rate, or the air flow rate required to meet applicable code or accreditation standards, whichever is greater. The fan power for System Type 9 or 10 should be 0.3 Watts per cfm of Baseline heating supply airflow. Should the system include a fan to provide non-mechanical cooling (i.e. increased fan air flow rates set to operate once indoor or outdoor temperature exceed a certain temperature, or direct or indirect evaporative cooling), the Baseline model should also include a separate fan to provide non-mechanical cooling, sized and controlled the same as the Proposed design. For non-mechanical cooling fans, the Baseline fan power should be modeled as 0.054 Watts per cfm of non-mechanical cooling airflow.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.