We have old existing office building where ducted FCU is serving all the spaces. Fresh air is dumped to the plenum (no ducts), likewise for return air, so mixing happen randomly within the ceiling plenum.
We have measured the fresh air at each level before it is discharged to the plenum, we have also measured the discharge at each zone terminal unit.
Our total fresh air is more than enough on floor level, however, for the ASHRAE 62.1 calculator we still need to input the primary air for each zone, so my question is: what is the reasonable / conservative ratio (zone primary air / zone discharge air) that LEED would accept? knowing that this is our second submission so no room for errors :D
Much appreciated
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
The previous comments were related to doing the measurements of "fresh air" at each air handler's level, since we had done measurements of "total air flow" and assumed 20% for it to be fresh air, which is common practice for Singapore. But since GBCI commented on measuring only "fresh air", we are now doing measurements at system level fresh air duct. However, in the multiple zone table in the LEED calculator, we still require to fill in "primary airflow" values for each space, even if the system level fresh air is complying.