CS-v4 EAc5:Renewable energy production

RE: v.4 Core & Shell - RECs as Offsite Power

Hi LEED user, 

We have a C&S project includes retail and office towers with limited space for renewable power generation. 

The utilities company in the area has just launched the REC porgramme and the project could participate by simulating the green power deamand. 

So for our C&S building, at least 15% the total buidling energy cost will be is adopted for calculation. The Project is planning to purchase the REC from local utilities company with a 10 year contract for the building energy cost of 5%. Would that achieve 3 points under EAc5?

Besides, the Project also planned to purchase REC from green e energy certified supplier with a 5 year contract, in which 100% ofC&S buidling's energy could be offset. As such, 2 points are anticipated under EAc Green Power and Carbon Offset. 

Please help to clarify. 

Regards, 

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 02/10/2023 - 20:43

RECs do not contribute to the Renewable Energy Production credit under LEED v4.0. So no points are possible relative to what you have described. The RECs can count under the Carbon Offsets and Green Power and based on what you wrote would qualify for two points. You should also look at LEED v4.1 as you might be able to pick up an additional point in the credit that combines these two.