From where can i take rated power for equipments like laptop , i read it on laptop about 55wh then i divded it by work hours give me 6.7watt , is that right ??????
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium for $... »
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5931 thumbs up
May 19, 2015 - 11:23 am
Name plate data for many electronic devices will be inaccurate. Your value sounds low for a laptop.
Michael Smithing
Director - Green Building AdvisoryColliers International Ltd.
304 thumbs up
May 20, 2015 - 12:32 am
You definitely should not divide by work hours - the form requires the rated power - which is the value on the name plate. You might check the technical specification for the product online.
Yaser Al Sharif
Roya12 thumbs up
May 20, 2015 - 2:15 am
but the nameplate on laptop give me the rated power in watt houre , the form on leedonline asks for rated power in watt so i should convert it from watt hour to watt by divided it on the works hour , right ????
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5931 thumbs up
May 20, 2015 - 12:51 pm
I generally do not see watt hours on the name plate. There is usually a watt value or sometimes volts and amps for larger equipment.