Hello. I had a question about who can fill the role as the CxA for the enhanced credit. The case is where an engineering firm was hired by the architect to complete the civil/land development work. Can the same engineering firm also be hired by the owner to be the enhanced CxA to complete the commissioning of the MEP systems?
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium for
Emily Purcell
Sustainable Design LeadCannonDesign
LEEDuser Expert
309 thumbs up
February 27, 2020 - 12:13 pm
I asked GBCI this question about a month ago, just followed up to check on the response...will let you know what I hear. Our project is in the exact same situation, reviewing Cx proposals including one from the firm handling the civil work.
Summer Minchew
Managing PartnerEcoimpact Consulting
LEEDuser Expert
163 thumbs up
February 28, 2020 - 1:40 pm
I had a similar situation on a v2009 project (same firm but completely separate teams doing civil design and fundamental and enhanced commissioning) and it was fine. Will be following to see if there are any changes per v4.
Scott Bowman
LEED FellowIntegrated Design + Energy Advisors, LLC
LEEDuser Expert
519 thumbs up
February 28, 2020 - 3:14 pm
Interesting response, Summer. I would not have thought this would work as civil engineering is definitely part of the design team. While I agree that this does not pose any real practice problems (assuming the firm has the required experience of course), it would seem to raise a red flag with GBCI in my opinion. Also, not sure how much attention reviewers would be paying on this kind of arrangement as they would for the MEP engineer doing the Cx.
Emily Purcell
Sustainable Design LeadCannonDesign
LEEDuser Expert
309 thumbs up
March 4, 2020 - 6:17 pm
Hi, we had GBCI confirm that the same firm cannot provide civil and Cx. The financial relationship means it is not an independent 3rd party even though the work is separate.
A.J. Speicher
Commissioning Project ManagerBorton-Lawson
March 7, 2020 - 7:50 am
Thanks for the response Emily!