FAQs about EAp2 :

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

View answers »

Forum discussion

CS-2009 EAp2:Minimum Energy Performance

Pump consumption

I have a proposed design with boiler and chiller, with water distribution. There are many pumps in the distribution system. In the other hand, I have a baseline building with a system 5 (VAV) and a hot loop with a boiler. This baseline only has a pump in the hot loop. eQuest results says that there is more consumption for Pumps and AUX for the baseline than for the proposed. This shouldn't be like this, I guess. What do you think? Reasons? Thank you in advance.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 09/09/2014 - 15:01

There are several variables so it is hard to say without the specific data. Are the Proposed pumps variable speed?

Tue, 09/09/2014 - 18:58

Marcus, yes, hot water loop and cold water loop have VS pumps. The basline building has just one pump, for the hot water loop, but there is no pump for the cold water loop, as it has been defined as a VAV system.

Tue, 09/09/2014 - 19:26

Variable speed versus constant speed can have a large energy impact. Depending on the difference in kW this may explain your result.

Wed, 09/10/2014 - 09:48

Have you considered paragraph G3.1.3.5 "Hot water pumps" for the baseline model? Regards

Mon, 09/15/2014 - 08:29

Thanks Marcus and Francesco, Yes, Francesco, I have considered that paragraph G3.1.3.5., but it seems to me too few pumps in the baseline... One more question, this hot water pump for the baseline, has to be equivalent to....?? the primary loop pumps? primary and secondary loop pumps? Thanks guys, you are really helping me!

Mon, 09/15/2014 - 10:07

G3.1.3.5.: "The pumping system shall be modeled as primary-only"