Hi, we are looking for a Public lavatory (restroom) faucet with water sense label but all we have found have higher consuption that the base line.
Can we apply for this prerrequisite with faucet without Water Sense Label.
Forum discussion
CI-v4 WEp1: Indoor water use reduction
Hi, we are looking for a Public lavatory (restroom) faucet with water sense label but all we have found have higher consuption that the base line.
Can we apply for this prerrequisite with faucet without Water Sense Label.
LEEDuser is supported by our premium members, not by advertisers.
Go premium forTo post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.
Bipin Karki
Project Manager - Sustainability Division84 thumbs up
August 25, 2019 - 11:28 am
Hello Carlos,
For an international project, you can apply this prerequisite without WaterSense Label. Please see the guidance here: https://www.usgbc.org/sites/default/files/GBC_016%20WaterSense%20Rd3-1.pdf.
Also, for not listed countries without a listed labeling program must meet the flush and flow requirements of “Table 6. Maximum installed flush or flow rates for prescriptive path” listed in the Step-by-Step Guidance section of the LEED Reference Guide.
Hope this helps!