Forum discussion

Healthcare-v4 WEp2:Indoor water use reduction

Public fixtures and private fixtures

Does it make sense to break out into two groups? one for public toilets/ lavatories and second group for private toilets and lavatories?

or would it work fine to be just one group to calculate reduction of water usage with the total number of FTE's and visitors?

 

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 03/22/2018 - 19:02

It looks like the credit language only breaks the faucets into public and private. I would assume this means you should not do so for toilets?

Thu, 03/22/2018 - 19:38

It depends on how you are defining occupancy and if you can keep things consistent between the different forms. Specific to private versus public toilets in hospitals, I usually have broken them out into separate groups. Inpatient rooms are 'private' and their use rates vary from an outpatient or staff use. For example, you can tweak the number of showers per day based on the care level and zero out the kitchen sink use. Typically I use the 'resident' tag for inpatients. It is easy to keep inpatient separate in your occupancy calculations and those PI forms. Just be clear and consistent.