FAQs about EAp2 :

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

View answers »

Forum discussion

NC-2009 EAp2:Minimum Energy Performance

Proposed v Baseline Outdoor air

I am working on a multifamily building. The proposed system is a Rooftop unit with constant vlume and 100% outdoor air. No return or exhaust and a set SA CFM. My question is whether in this case, since the supply air and the ventilation CFM are equal; I should model the baseline supply air CFM with the calculated CFM, based on the 20 degree delta T, or using the same SA CFM as in the proposed building. Please reply Thanks

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 06/14/2013 - 19:01

The baseline needs to follow the Appendix G rules. So it is a system 1 or 2 and it needs to be auto-sized by the software according to G3.1.2.8.

Wed, 07/10/2013 - 06:08

Related question...for a naturally ventilated building without "mechanical" cooling: 1) the "mechanical" ventilation requirement of both proposed and baseline models is zero, as the ventilation is done via windows in both proposed and baseline models. 2) the proposed model includes the baseline system for cooling which jumps on when the "natural" cooling via windows cannot hold setpoint (all be it never as we can set the setpoint for cooling high enough...although I prefer to keep with the intent of 90.1 to provide cooling when user thermal comfort is in jeopardy...bearing in mind that statistical users 10% "dissatisfied" are at different temperatures, i.e. more extreme, in naturally ventilated spaces...ASHRAE 55, AM 10). Note: The cooling system includes the entire cooling system...possibly with economizer, heat recovery, etc. Q) G3.1.2.4 Fan System Operation Will the baseline and proposed fans both come on continously during occupied hours? As the minimum "mechanical" ODA is set to zero, this fan will basically be mindlessly blowing air in circles during the non-heating occupied hours. My opinion is that fans should be set to cycle to meet loads in both models. As G3.1.2.4 is a baseline requirement, the best outcome for credit would be to set the proposed case to cycle and the baseline case to be continous during occupation hours.

Wed, 07/10/2013 - 13:54

We agree with your opinion. Without mechanical ventilation the fans should cycle in both models all the time.

Thu, 07/11/2013 - 08:22

thanks