CI-2009 EAc1.3:Optimize energy performance - HVAC

Project Scope and Tenant Scope

Another one I can´t quite get my head around. Our client will be the sole tenant in a small commercial building. The owner has provided a VRF system complete with the condensers and evaporators (the space has never been occupied). Our preliminary review suggests that the system will comply with the ASHRAE and NBI requirements.but if the tenant does nothing more than install proper zone ductwork and controls can they achieve the Equipment Efficiency portion of this credit?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 04/11/2014 - 17:16

Thiago, that is correct - you would be meeting the credit requirement under the third option of interpretation #10134. But note that you must also provide load calculations that meet the requirements of the credit.