FAQs about EAp2 :

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

Process Energy for Manufacturing facility

I have seen several posts pertaining to process energy and how it should be modeled, but I am still unclear as to how it should be treated pertaining to manufacturing process energy. I am modeling a manufacturing facility, an estimated 80% of the energy consumed is done so by equipment that is used to manufacture a product. ASHRAE 90.1 states that the provisions of the standard do not apply to "equipment and portions of building systems that use energy primarily to provide for industrial, manufacturing, or commercial processes" meaning that those processes are not regulated as a part of ASHRAE 90.1. The LEED NC reference guide defines process energy on page 258 and uses the language "...but not limited to..." perhaps intending to encompass other sources of process energy? My question is, in order to adequately model the aforemnetioned manufacturing facility for LEED NC, do I have to model the process energy used in manufacturing processes? i.e. (process boilers, process cooling equipment, presses, curing systems, presses...etc) Or can I simply omit this process equipment and model the building as any other building, with standard process loads for the space type and include all equipment regulated by ASHRAE 90.1? If modeling manufacturing process energy is required, what are acceptable means for developing a baseline for the process energy, outside of metering each piece of equipment in an existing facility?

1

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 05/03/2012 - 05:53

Yes you must model the manufacturing equipment. The Baseline would be standard industry practice for that process. You and your owner will need to establish and defend that you have developed an appropriate baseline and are claiming reasonable savings against it.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.