FAQs about EAp2 :

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

View answers »

Forum discussion

Schools-2009 EAp2:Minimum energy performance

Pressure Drop credit for DOAS system in Baseline

Hi.

 

We are doing a school building Energy modelling. In this school building we used FCU+ DOAS system. DOAS unit has (1) merv 13 for both OA and EA (2) DOAS has ER device and heat pipes.

In baseline, I created five systems, three are System 5 and two of them are system 3. 

(1)Per ASHRAE 90.1 2007, I dont need Energy recovery device in the baseline. So can I take PDC for Energy recovery device and Heat pipe for ventilation air?

Or I can take PDC for Energy recovery device and heat pipes only when I have ERV in the baseline.

(2) If I can take PDC then okay but if I cant then is there any way to consider this PD in baseline?

Manish,

 

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 08/11/2022 - 14:45

(1) No, according to the footnote to Table G3.1.2.9 you can only include pressure drop adjustments for heat recovery devices which are required in the Baseline by Section G3.1.2.10 (2) No, essentially you get to take the credit for the recovered thermal energy but you need to pay the fan energy penalty that goes along with it