Hi All,
I am in a state of dilemma for submitting the building envelope parameters to the design team during tender stage of a project. The U values and SHGC factors are being asked by architect team to compare proposed envelope design against ASHRAE 90.1 in every tender project. And the same U value and SHGC factors are being taken forward by HVAC design team to size the systems in HAP.
In this case, being from the sustainability team, do we refer the values based on prescriptive compliance path or do we directly refer the baseline values as per Appendix G in ASHRAE 90.1?
Please Note: The initial proposed envelope details are shared to us for comparison.
Your clarifications & suggestions are greatly appreciated.
Jamy Bacchus
Associate PrincipalME Engineers
29 thumbs up
February 14, 2025 - 1:42 pm
Hi Anurag,
For the EAp2 prereq in v4.1 you can demonstrate compliance with 90.1-2016 via prescriptive, ECB in Section 11 or PRM in Appendix G. Which of these paths is the design team planning to use for LEED?
If you're going perscriptive, then you'll need to be at least as good as the glazing tables for your climate zone in the envelope tables in Section 5.5 (if we ignore Envelope Tradeoffs in 5.6).
If you're using a performance path, then the glazing in the model's baseline is from Table 5.5x for ECB or Table G3.4-x for PRM.
You won't want to tell the design team the values in Appendix G as those are for the 2004 stable baseline and you'll have to beat those by a decent margin, so don't send the team those as it will misled them.
Jamy
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5931 thumbs up
February 14, 2025 - 1:49 pm
I assume this is the same project you have been asking about in other forums? For a LEED project you should be doing early stage energy modeling to evaluate your options and inform those selections (you do not need to know all about the design in order to model it as that misses the whole point of energy modeling). Looking at window performance values in isolation will not give you very well informed answers regarding energy performance. You should be doing early stage energy modeling to evaluate bundles of interrelated strategies to optimze the whole building performance. What is the project's energy goal?
Anurag Ghosh
Assistant Sustainability ManagerL&T Construction
1 thumbs up
February 14, 2025 - 9:08 pm
Hi Jamy & Marcus,
Appreciate your clarifications on the above.
So first answering to Jamy's question: We as a sustainability team always go for a compliance using PRM in Appendix G as that gives us a leeway for trading off between various sections. However, the architect and HVAC team often goes through a iteration of proposed envelope options to conclude upon the design factor. We are asked to compare the U values with ASHRAE 90.1 standard to establish a compliance. I am too very skeptical to provide values from table G3.4-x in appendix G for comparison as those values seem to be unideal from design perspective. And the same thing goes with selecting the Lighting and HVAC systems for a minimum energy performance and therby also optimizing the performance using various controls. What I generally do is taking the values from Section 5.5-x for comparison to be on the conservative side for design team. What are your views on this?
Now, answering to Marcus question: The project is targetting for a LEED Platinum & Net Zero by 2030. The main challenges we find during this early tender design stage of a project is unavailability of many inputs(including the floor plans,elevation & section drawings) which restricts us in performing a whole building energy modelling. So, we basically follow an established set of strategies to circulate to the design team (hands are tied due to unavailability of inputs). Strategies like LPD to be 30-40% less than ASHRAE 90.1 values, occupancy sensors/timer controls, VAV systems, Heat Recovery Systems, Variable flow Cooling Towers(if water cooled chiller used), and so on. What are your suggestions in such cases?
Jamy Bacchus
Associate PrincipalME Engineers
29 thumbs up
February 14, 2025 - 11:44 pm
I generally agree with your approach. You don't have exact criteria and data. You can do sensitivity studies and identify ECMs per ASHRAE Std 209-2024.
But there is zero value in giving the design team the 90.1-2004 Appendix G values ...unless you want to include the BPF applicable to your building type and climate zone along with your targeted EAc2 points/savings. What good is it to tell them a 20-yr old code minimum when you're targeting net zero?
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5931 thumbs up
February 17, 2025 - 11:38 am
I don't agree with your approach as it includes some assumptions that in my experience are not accurate and actually harmful when designing a net positive energy project.
I will once again challenge the notion that you have to have floor plans, elevations and sections to create a sueful energy model. We use eQUEST but this is not exclusive to that software. There is a "wizard" mode where I can go through about 30 screens of inputs and create a model that is representative of what is intended to be designed. This can usually be done in less than 2 hours. It is likely that in the very beginning you know the building type, there is a building program so you know rough areas, you likely know how many floors it is likely to be, etc. You can use what you know to create these early stage models and use them to help guide design decision-making including building massing, orientation and configuration. If you are waiting for a mostly completed architectural design then it is too late to use the energy model to guide design decisions and you are left with the ablity to make only small incremental improvements.
A net positive project requires a different approach if you want to do it in the most cost effective manner possible. For these types of projects we establish an EUI goal. For most exteranl load dominant commercial buildings we often start with around 15 kBTU/sf-yr. We apply green building design strategies like proper orientation, exemplary daylighting, massing and shading strategies, etc., in other words passive design strategies. You must impact the building design, not just the systems design within it. Once you implement strategies to reduce the building's loads you then select and optimize the HVAC system. We create a miximum potential model in the very beginning that significantly exceeds code minimum values. We start from there and then iteratively work our way back as necessary. If you start with code values and try to work your way up you will never get to a fully optimized approach in my experience. If you don't account for the impact of the building design on the loads you won't get there either.
Anurag Ghosh
Assistant Sustainability ManagerL&T Construction
1 thumbs up
February 18, 2025 - 12:34 am
Hi Marcus, I completely get it now. We basically use Design Builder software for energy modelling. So, you mean to say that we should initially work with conceptual models( basically what we call a box model in designbuilder) iteratively to impact the building design in every possible way during tender. This inlcudes but not limited to the envelope selection, orientation, massing to create an impact on the building design along with the design team. The box model will be having approximate conditioned areas distributed by no of floors and the vertical glazing % and skylight % will be distributed as intended ( we do have an option to set the % in design builder). Thereafter, the systems within inluding HVAC to be worked upon with the design team for a final impact. Please correct me if I am going on the wrong path?
Also, can you provide some reference codes for EUI figures based on various building typologies and intended net positive design like you did mention in the last thread?
Jamy Bacchus
Associate PrincipalME Engineers
29 thumbs up
February 18, 2025 - 2:39 am
I don't believe you've mentioned what type of building you're working on, its solar access, the number of floors and what ASHRAE 169 climate zone it's in. Here are 3 free prescriptive net zero guides which might be useful depending on your project:
https://www.ashrae.org/technical-resources/aedgs/zero-energy-aedg-free-d...
Also worth a read is Charles Eley's 2017 ASHRAE Journal article on net zero potential:
https://www.eley.com/sites/default/files/pdfs/ASHRAE_Journal_July_2017_[...
You mentioned the project is: targetting for a LEED Platinum & Net Zero by 2030.
I'm going to assume since you're asking a NC v4.1 question you're using LEED v4 or v4.1 BD+C for that Platinum target, but I have zero idea which net zero definition or certification you're using and if it's energy or carbon. LEED Zero includes options for energy or carbon for existing buildings--not new--and includes user transportation and operational emissions for a single year but omits embodied carbon. ILFI has different boundary conditions in its energy or carbon certifications. While I have luke warm support for many of these systems or ratings which wholly ignore entire GHG emissions portions, I would encourage your team to review ASHRAE Standard 240P--either the draft version or hopefully the final version when it's released later this year for a Whole Life Carbon approach to zero carbon.
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5931 thumbs up
February 18, 2025 - 11:52 am
Sounds like you understand. To design a net positive project cost-effectively it needs to be super energy efficient. Most energy efficiency strategies are still cheaper than solar panels. So you need to reduce energy use dramatically. Every kWh saved is one less that you have to produce, so the solar system gets smaller and cheaper. When evaluating the economics you have to take this into account.
There are sources for US based projects but I am not sure about availability in other parts of the world. In the US we access the CBECS data from the US Department of Energy and this data is accessible through the US EPA's Target Finder tool. This data does not really apply outside the US. You can also obtain this information from existing building projects, maybe others you have worked on and calculate the EUI to get an idea of where your projects stack up.