It is not clear from G3.1.3.19 where the preheat coil should be placed.
Is it upstream or downstream the economizer and the heat exchanger?
Forum discussion
NC-v4.1 EAp2: Minimum Energy Performance
Hi,
It is not clear from G3.1.3.19 where the preheat coil should be placed.
Is it upstream or downstream the economizer and the heat exchanger?
LEEDuser is supported by our premium members, not by advertisers.
Go premium forTo post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.
Samer Hassanie
Energy Consultant1 thumbs up
February 6, 2024 - 7:16 am
This question is regarding ASHRAE 90.1 2016.
According to COMNET, the coil has to be placed in the outdoor air stream, while according to the user manual ANSI/ASHRAE/IES Standard 90.1-2016 Performance Rating Method Reference Manual (pnnl.gov) the coil has to be placed in the mixed air stream. Which source is more reliable?
Luis Andrade
2 thumbs up
February 8, 2024 - 8:35 am
Hi Samer,
Having in mind that this is part of an Energy Efficiency standard, I would think it would be logic to place it on the outdoor air stream but only after the heat recovery. Heat recovery would "do its job" and only then, if needed, the pre-heat would "kick-in".
As per having a heating coil in the mixed airstream, I guess that you already do for systems 5-8, so indeed you need to have 2 coils:
1) pre-heat coil in outdoor branch after heat recovery with setpoint of 11ºC dT difference to heating setpoint;
2) Heating coil after the mixing box (without a standared defined setpoint) to make sure you don't suply unconfortable temperatures (probably, the same as the LAT from the main cooling coil;
That's my view and I hope it helps!
Samer Hassanie
Energy Consultant1 thumbs up
February 9, 2024 - 9:08 am
Thank you Luis for the reply, but I can see little difference in both modes you described when it comes to the energy use.
Luis Andrade
2 thumbs up
February 12, 2024 - 6:30 am
Hi Samer,
Thank you for commenting. Sorry if I wasn't clear about it. Regarding energy efficiency, it is clear to me that having a fixed pre-heat coil before or after the energy recovery could make a huge difference in energy consumption (depends on your climate zone, obviously). I would say the difference is more than little...
As for before or after the mixing box, my point is: the pre-heat coil has a fixed LAT setpoint and should be 11ºC less than heating setpoint (ususally 10ºC as setpoint usually is 21ºC) and, from where I see it, should be before the mixing box (regardless of energy use). 10ºC is a temperature of disconfort when supplied to a space, so there should be another heating coil after the mixing box that heats the temperature just enought to avoid the disconfort (usually, matching the LAT for cooling).
Not sure if you agree, but there it is my opinion, hehe.
Thank you!
Samer Hassanie
Energy Consultant1 thumbs up
March 4, 2024 - 6:50 am
Yes, my comment was regarding the two cases presented (before or after the mixing box).
My confusion was mainly driven by whether I should have two preheat coils, since previously I have been including preheat coils in the mixed airstream since most of the proposed buildings included preheat coils. Now, I got it confirmed that there should be only one preheat coil.
Thanks for discussing this.