Forum discussion

NC-2009 WEp1:Water Use Reduction—20% Reduction

pre-rinse spray faucet

Working on my 1st project that includes a pre-rinse spray faucet for a restaurant/cafe type setting. What should should be shown as the total daily uses and the duration on the template? We know the gpm.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 08/14/2013 - 18:51

Hi Sheryl, The LEED Reference Guide for Green Building Design and Construction, 2009 Edition (Updated June 2010) 11/1/2011 Addenda clarifies that for projects with commercial pre‐rinse spray valves, there is no longer a baseline performance standard from which to claim savings; rather, the prerequisite requires only that the flow rate comply with the ASME A112.18.1 standard of 1.6 gpm or less. Hope helpful!