Working on my 1st project that includes a pre-rinse spray faucet for a restaurant/cafe type setting. What should should be shown as the total daily uses and the duration on the template? We know the gpm.
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium for
Carlie Bullock-Jones
PrincipalEcoworks Studio
LEEDuser Expert
220 thumbs up
August 14, 2013 - 2:51 pm
Hi Sheryl,
The LEED Reference Guide for Green Building Design and Construction, 2009 Edition (Updated June 2010) 11/1/2011 Addenda clarifies that for projects with commercial pre‐rinse spray valves, there is no longer a baseline performance standard from which to claim savings; rather, the prerequisite requires only that the flow rate comply with the ASME A112.18.1 standard of 1.6 gpm or less.
Hope helpful!