Dear Sir/Madam,
per G3.1.3.10, the baseline bulidnging design pump power shall be 349kW/1000 L/s. when the chilled-water system is a primary/secondary system, there will be primary pump and secondary pump. shall the sum of the primary pump and secondary pump be 349kW/1000 L/s or each pump be so?
Regards,
Tiantian
Beijing,China.
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5907 thumbs up
September 23, 2013 - 10:29 am
It is the total of the two. There was an ASHRAE Interpretation last year which clarified this issue. You can download the interpretations from this web site - http://www.techstreet.com/products/1608726 - this particular one is IC 14.
tiantian zhou
September 23, 2013 - 10:04 pm
Thank you,sir.
Later I can first ask for help to the web site for the least trouble to you.
if the web site can have a direct descripation for each interpretation on the home page, it is so great.
Thank you again.