In LEED 4.0 it states that for plumbing all Domestic Hot Water Systems, pumps and controls. Is this saying all plumbing pumps (sewage ejector, domestic water booster, etc) are required or only pumps dedicated to the Domestic Hot Water systems?
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium for
Scott Bowman
LEED FellowIntegrated Design + Energy Advisors, LLC
LEEDuser Expert
519 thumbs up
March 5, 2014 - 8:01 am
Unfortunately I am going to have to say “maybe”. Reading the v4 guide does not give much more definition, saying under systems that must be commissioned: “Plumbing, including domestic hot water systems, pumps, and controls”. There is no mention of what is not included. Traditionally, I have focused on those systems that can be commissioned and that consume more energy if there is something not programmed or installed correctly. Everything related to domestic hot water is for sure. Pressure boosters are worthy of testing as well.
While I have not considered the sewage ejectors or sump pumps to be under LEED scope, we have traditionally tested high water alarms that are often tied into the DDC system, and making sure that floats or sensors are in correct positions to operate pumps in the correct order.
In my opinion, and that is all it is, everything with DHW, pressure boosters, rainwater capture, sensor faucets = YES. Sewage ejectors, sump pumps = NO, but good to do.
Gabriela Crespo
BECxP, CxA+BE, LEED AP BD+C, O+MRevitaliza Consultores
20 thumbs up
October 20, 2016 - 3:12 pm
Hi Scott!
Would water treatment plants be included?
Thanks!
Scott Bowman
LEED FellowIntegrated Design + Energy Advisors, LLC
LEEDuser Expert
519 thumbs up
October 21, 2016 - 1:41 pm
If the water treatment plant (either water coming in or going out) is part of the building systems, then I would think yes, they should be included. Typically these kinds of systems have significant requirements for testing and reporting for performance and code issues, so good collaboration with the AHJ would be important so tasks are completed correctly.
Gabriela Crespo
BECxP, CxA+BE, LEED AP BD+C, O+MRevitaliza Consultores
20 thumbs up
October 21, 2016 - 1:50 pm
Thank you Scott!