What happens if my WFA*VT is too large because my bay is only as deep as to the back wall? Do I have too much window and therefor don't have good daylighting? WFA*VT Should be 0.15 to 0.18

4

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 08/18/2011 - 12:52

The prescriptive method should not be used to determine whether you have good daylight or not. What if that space is north facing in a northern climate that has alot of overcast days? You may have to provide more glazing with a higher VLT to meet the daylight needs year round. Since the prescriptive method is a general formula, the formula is what it is. You can try and break up the space into multiple daylight zones, but that may make it worse. I would recommend simulation, there are some free downloads of daylight simulation programs such as SPOT that can help you. I would not change a design based on meeting the requirements of the prescriptive method.