Perimeter light levels affected by surrounding sites.

The perimeter light levels are driven by the surrounding light sources such as street lights and adjoining building lights.  Do I need to make note of these factors in the credit form?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 08/05/2022 - 13:38

If you are following option 2, you measure the perimeter twice.  Once with the project's exterior lights on, and a second time without.  Both measurements will include the sourrounding light sources as you noted.  The purpose of this option #2 in the credit is to show the surrounding light sources makes up the vast majority of the light on the perimeter, and that this LEED project makes up a small portion. 