FAQs about EAp2 :

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

Parking garage ventilation - Proposed vs. Baseline

Hi Markus, Following our correspondence as of Jul/13/2017, we've modeled the garage ventilation claiming some energy savings. We've provided explanation reflecting all details including all considerations related to CIR 10371. The reviewer's reply however is stating (quoted): "…parking garage spaces must include a minimum of 0.75 cfm/ft2 of ventilation/exhaust air flow… Provide documentation to verify that the minimum exhaust rates outlines in Table 6-4 are reflected for the parking garage spaces in the actual design" CIR 10371 is stating that the Proposed case shall reflect the actual design…. Our impression is that the reviewer probably didn't allocate our explanation among the numerous attachments (the project is very big though). Our explanation was like this (quoted): "While modeling the Garage ventilation, the following considerations were taken, including those of CIR 10371. 1. Proposed case 1.1. Proposed case is reflecting the actual design, which is in accordance to the local norms 1.2. Proposed case is provided with control ventilation strategies, capable to automatically detect contamination levels of concern on parking garages - CO in this case. Below, an extract from the project documentation is illustrating these intentions. 1.3. The exact location of these CO sensors will be provided in the construction documentation and their proper functioning will be verified during the Commissioning procedure. 1.4. Proposed case is modeled such that a minimum air flow of 0.05 cfm/square foot is maintained. 1.5. Propose case is not claiming energy savings more than 75%. 2. Baseline case 2.1. The Baseline case fan volume is set to comply to the minimum required ASHRAE 62.1 parking ventilation rates of 0.75 cfm/square foot. 2.2. Baseline system fan power is calculated at 0.3 watts per cfm. 2.3. Baseline ventilation is arranged with DCV control and it operates upon schedule which is reflecting a typical behavior of such control. 3. Extracts from the project design concept related to Garage ventilation …….. Car park ventilation systems During the winter and transitional period within the daytime the system is working with heating coils, which is activated upon zone's temperature settings. During the summer time this coil is off. The ventilation system is not functioning during the night, weekends and holidays. Control of the degree of air pollution in the parking lot In the compartments of the parking lot, the CO sensors monitor the degree of air pollution from the exhaust gases. When a pollution level of 20 mg / m3 is established in some compartment, any of the CO sensors in this compartment will send a signal to the BAS and the exhaust fan servicing the compartment (if it was turned off) is turned on. Disconnection of this exhaust fan is carried out with a decrease in CO concentration below 20 mg / m3. ………." Could you please take a look and advice - is it something wrong there, should we do some rewording and to upload it within the reply. Thanks a lot for your support.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 08/02/2017 - 15:41

Is is very hard to say what the reviewer is looking for without seeing the whole comment. I don't know what was in Table 6-4, but that sentence alone indicates that they want to see additional documentation to confirm the minimum exhaust rates in the proposed design. I am not sure how that connects, or not, to the partial sentence before it. What you submitted appears to be mostly correct. The one odd item is 2.3. I am not sure why you have DCV in the baseline?

Thu, 08/03/2017 - 08:11

Hi Marcus, Thanks for your reply. The whole comment of the reviewer (technical advice 2. to IEQp1) is: "It is unclear if the parking garage spaces are ventilated in accordance with Table 6-4 of ASHRAE Standard 62.1-2007. Note that Table 6-4 requires that parking garage spaces must include a minimum of 0.75 cfm per square foot (3.8 L/s per square meter) of ventilation/exhaust airflow, unless two or more sides of the parking garage are comprised of walls that are 50% open to the outdoors. Provide documentation to verify that the minimum exhaust rates outlined in Table 6-4 are reflected for the parking garage spaces in the actual design." In item 2.4 of our explanation a DCV was added because when filling-in the MEPCalculator, in the tab "Process Loads", in the section Garage Fan Power Calculation upon checking the condition "Credit is taken for garage fan power", in the Note 1. is written: "The Baseline parking area must meet the requirements of ASHRAE 90.1-2010, Section 6.4.3.4.5 which establish mandatory Demand Controlled Ventilation (DCV)." So, we've created a schedule most likely close to the Proposed ones, meaning that the system will not be activated during weekends and holidays (EFLH 1963). Because of providing the needed data in this section, we didn't prepare an Exceptional Calculation Method, but just created all the explanation I've send you in the previous mail as an attachment named "Garage Fan Power" and in the section Special Circumstances of the EAp2 form we've noted about this issue and the associated with it attachment. I agree that the Proposed garage air flow rate is much smaller than in the Baseline and this is the only reason why the Outdoor air flows are not equal between the Proposed and Baseline (which is another remark we have to address), but the Proposed is made in accordance to the local codes, besides there are separate Smoke exhaust ventilation specifically to the garage areas, which airflow rate is 5.6 L/s.m2. We didn't simulated the whole smoke exhaust ventilations (it is a separate schedule) as these are an emergency only activated systems. So, how should we approach by replying to the reviewer? Should we upload again our explanation integrated as a Reply to reviewer's comment (if some rewording needed, please advice) or should we insist the client for a complete redesign of the whole garage systems. As I've mentioned before, probably the reviewer didn't noticed our explanation, because the project is a huge one (about 70 HVAC systems in the Proposed) with lots of attachments (which are required though) and the reviewer's reply came after 10 working days after the design review application. Your advice will be highly appreciated. Thanks.

Tue, 08/08/2017 - 08:48

Hi Markus, Probably you didn't have a time to read the long reply I've send you (with the idea of providing you the needed info), but what actually I'd like to understand is: For parking garage ventilation (Proposed), should we apply the requirement of a minimum air flow rate of 0.75 cfm/ft2 as a mandatory condition? When we create the Baseline model - yes, but CIR 10371 states that Proposed case is reflecting the actual design, meaning that these air flows (Propose and Baseline) will very seldom be equal, which is facing another remark - the one for an equal OA flows, because all parking garages are 100% OA. Your opinion is highly appreciated. Thanks.

Wed, 08/09/2017 - 15:42

It sounds like you are dealing with comments in both IEQp1 and EAp2. For IEQp1, the reviewer is asking you to verify that the requirement of 0.75 cfm/ft2 can be met by the design exhaust system (at peak capacity). DCV in parking garages is a very common strategy in LEED projects and is certainly acceptable for IEQp1. In responding to the IEQp1 comment you could demonstrate that the project complies with the 2009 International Mechanical Code Section 404, which requires that the exhaust system be capable of 0.75 cfm/ft2 but may operate as low as 0.05 cfm/ft2. For EAp2 it sounds like the reviewer might be questioning a difference in OA flows reported in the Air-Side HVAC tab of the MEPC. Parking garage exhaust is not typically reported here but instead should be reported in the Process Loads tab to avoid confusion, then the OA flows in the Air-Side HVAC tab would be identical.

Thu, 08/10/2017 - 05:39

Thanks for the reply Tyler, It clears a lot. The only reason that the garage ventilation was included in the MEPC was because it has some kind of heating - heating coils activated only when the space temperature falls below 5 deg C (41 F), so if reported as Process loads how the heating load should be reported. One final question: Since it is required that Baseline should have also DCV, should the DCV operating schedules be identical. Thanks

Thu, 08/10/2017 - 18:27

I would keep the exhaust fan inputs in the Process loads tab and report the heating system only (without the exhaust airflow) in the air-side HVAC tab. The requirement for DCV indicated in the MEPC is only applicable to 90.1-2010, so that would not apply if this is a v3 project unless you are choosing to use 90.1-2010 with the adjusted point thresholds.

Thu, 08/10/2017 - 19:10

Hi Tyler, Thanks for your reply. In case however of v3 project (which actually our case is) what could be the Baseline operating schedule – is it going to be like 100% Available when DCV is not mandatory for this version? It could make the airflow rate difference even bigger and how it could be accepted by reviewers? Thanks

Fri, 08/11/2017 - 13:17

It looks like I was mistaken on my last reply. Since you are applying LI 10371, the Baseline is required to meet ASHRAE 90.1-2010 Section 6.4.3.4.5 which requires DCV even for v3 projects. However, this only requires the exhaust rates to be reduced by 50%, so the operating schedules may be different than the Proposed case (assuming the design DCV reduces the exhaust rates by more than 50%).

Fri, 08/11/2017 - 13:43

Thanks a lot. Now everything is perfectly clear. Appreciated very much.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.