Parking garage exhaust air rate - LEED CS v3

Hello, Our project has an underground parking garage. It is a non-occupied space since no one is working there. I could not find any parking or similar space in the Space Matrix (Oct 2013) table, so I'm not sure how to go about it. But, the Space Matrix states in Allowed Exclusions column, for IEQp1/IEQ2: "Nonoccupied spaces and restrooms are excluded from the Ventilation Rate Procedure (or natural ventilation) requirements". Does it mean than our parking garage is excluded from any calculation in IEQp1 and IEQ2? ASHRAE 62.1 defines a minimum exhaust air rate for parking garages, but the above statement overrides it in case of non-occupied parking garages, right? Thanks for your help!

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 04/02/2015 - 21:08

enclosed parking garages will need to comply with the exhaust rate listed in table 6-4 of ASHRAE 62.1.

Fri, 04/10/2015 - 09:26

Could you elaborate? Why the Space Matrix would not apply to parking garage?

Fri, 04/10/2015 - 12:41

The requirements of EQp1 outlined within the LEED reference guide require the project team to meet the minimum requirements of Sections 4 through 7 of ASHRAE 62.1. Section 6.2.8 of the standard requires exhaust per Table 6-4. Parking Garages are listed in this table and require an exhaust rate of 0.75 cfm/square foot. Similar to restrooms, parking garages are excluded from the ventilation rate procedure. However they are not excluded from the exhaust requirements outlined in Table 6-4. I hope this provides better guidance.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.