Parking garage with 2 sides of 6 sides 50% open to the outside

Table 6.4 of ASHRAE 60.1-2010 Note C states that for parking garages exhaust not required if two or more sides comprise walls that are at least 50% open to the outside. I have a garage with irregular geometry, it is not a rectangle but there are 6 sides (2 long sides, 1 medium sides, 3 short sides). Can the two walls that are at least 50% open to the outside be 2 of six sides, for example 1 long side and 1 short side of my parking garage?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 09/14/2023 - 00:50

The International Building Code explains this scenario a little better then ASHRAE. Google search "International Building Code 406.5". It considers total perimeter wall area and if the openings are located on two opposing sides of the garage. 