FAQs about EAp2 :

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

Parking garage

I have modeled parking garage in the simulation by taking 0.75 cfm/sf (exhaust)from ASHRAE 62.1-2007 which leads to energy consumpation of 43,450kWh. And in proposed case we are using CO sensor based parking garage due to which parking garage fans work for hardly 4 to 5 hours daily which leads to annual energy consumption of 20,850 kWh. Is it feasible to claim saving by this way?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 12/05/2012 - 15:08

Yes but make sure you follow the exceptional calculation in section 1.7 of the form. You will need to fully describe and justify all of your modeling (or calculation) assumptions and justify that this strategy is not required or standard practice in your location.

Wed, 12/05/2012 - 18:12

Thanks sir. instead of showing it in exceptional calc, i put it in table 1.8.1 & 1.8.2. In addition to this again 1 problem arised. EFLH of parking garage seems high i.e. 365x24 in baseline case. but in proposed case it comes around 365x5.5.EFLH in proposed case is lower because of CO sensors. Is it feasible to model parking garage to 365x24 hrs of operation in baseline?

Wed, 12/05/2012 - 21:18

Those sound like tables from the v2.2 template and not the LEED 2009 form? If you have the parking garage ventilation on a completely separate line item then it is OK to just provide the thorough description and explain your calculations without having to do the formal exceptional calculation. The baseline fan is constant volume but a 24 hour operation in the baseline would need to be justified in your narrative. Is the garage open 24/7? If not then 24 hour operation would not be justified.

Thu, 12/06/2012 - 07:16

you caught me. it is v3 project. I put those values in EAp2-4 and EAp2-5. Thank you so much.

Thu, 12/06/2012 - 22:04

I would reference the ASHRAE applications handbook to justify any CO based fan savings, otherwise you may get denied for claiming too much savings. See A15.19-21 and Figure 15 specifically. It provides backup data and examples.