Do parking spaces or restrooms need to comply with Ashare exhaust rates of table 'TABLE 6-4 Minimum Exhaust Rates'?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 04/26/2016 - 13:02

Exhaust fan testing is required. The tests must confirm proper function such as fan speed, voltage, control sequence and setpoints. The reference guide nor the credit template require the project team to confirm that the exhaust rates comply with TABLE 6-4. I have never been asked by a reviewer to confirm exhaust fan rates. This includes 100+ LEED EB projects and 2 LEED Volume Programs. If you do receive a request from a review team to confirm exhaust rates please post. thank you!