Hello, We did a paint VoC test with an independent party for a type of paint that one of our client is using (because the manufacturer didn't have technical documentation to provide us). The result summary looks like below. Acetone - Not detected (LOD 0.1ppm) p-Chlorobenzotrifluoride - Not detected (LOD 0.1ppm) Methyl Acetate - Not detected (LOD 0.1ppm) t-Butyl Acetate - Not detected (LOD 0.1ppm) Do you think this qualifies under the requirement for LEED?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 11/04/2013 - 01:37

Magda, that is just four specific VOCs. A VOC figure for LEED would include more than that—following the VOC standards listed in the credit language.