I need to know if both; Basecase and Proposed case should be identical meaning that both should be oversized with the same ratio? or the proposed case must be as designed without any oversizing ratio?
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium for
Erin Adkins
Executive DirectorEmpirical Energy Solutions
29 thumbs up
April 24, 2014 - 11:16 am
The only reason you should need to oversize the proposed is if you need to do so to reduce unmet hours in the proposed case.
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5909 thumbs up
April 24, 2014 - 2:07 pm
The Proposed is as designed. Baseline 115% cooling and 125% heating when auto-sizing the system capacities.