FAQs about EAp2 :

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

outdoor air unit system type

I have a project that is classified as a high rise residential building. In the proposed design, the living units are conditioned by water source heat pumps and ventilated via natural ventilation (operable windows). Four 100% -outside air units (each about 10,000 cfm) supply outside air directly into the corridors. Since we don’t plan to claim any energy savings from natural ventilation, I intend to model zero ventilation air in the living units both in the baseline and proposed case and the same amount of outside air (a sum of minimum exhaust rates for residential kitchens, bathrooms and dryers) introduced into corridors in both the baseline and proposed case. Question 1: What would be the appropriate baseline system for dedicated outdoor air units? Since our main baseline system is PTAC, I would use a constant volume system with DX cooling/air cooled condenser and hot water fossil fuel boiler as a heating source. Our design selection is a 100% outdoor air unit with DX cooling /evaporative-cooled condenser and natural gas heating. Are we allowed to take credit for evaporative-cooled condenser, or we are required to model the same condenser cooling source in the baseline and proposed case? For example, if we switch to 100% outside air water cooled heat pumps, should our baseline dedicated outdoor air system remain DX cooling/ air cooled condenser and hot water coil? Question 2: Can we use min exhaust rate per ASHRAE Table 6-4 and equation per Table G3.1.2.9 to size exhaust fans for unconditioned parking garage and take credit by comparing it against the proposed design BHP. I would greatly appreciate your opinion.

3

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 03/28/2011 - 13:28

For the baseline use system 1 or 2 for the entire building unless the exception in G3.1.1(a) applies. If it does reenter Table G3.1.1A and select the appropriate system. The baseline exhaust fans in the garage should be sized based upon the design rates and design exhaust fans power. Credit can be taken for improved motor efficiency. Table G3.1.2.9 only applies to fan power in conditioned spaces.

Mon, 03/28/2011 - 15:10

Marcus, Thank you for your input. Do you agree with me that the corridors providing access to residential apartments fall under "residential conditions" for the purpose of G3.1.1 (a)? I assume the baseline condenser cooling source should be identical to the one used in the proposed case. As opposed to ASHRAE Ch11, App G is not specific about this. Am I correct? Thank you.

Mon, 03/28/2011 - 21:28

Certainly debatable and it could be argued either way. I think the corridors are not residential since they do not fall in a living space and are common space. Table G3.1.1A is entered based on the heating source. So use the system it tells you to in the baseline and use the system you have designed in the proposed. Appendix G is a bit confusing on this subject. I have found that looking at 90.1-2010 can often help clarify the intent of the 90.1 committee related to 90.1-2004 or 2007 since some of these issues have been addressed.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.