Forum discussion

NC-2009 IEQc1:Outdoor Air Delivery Monitoring

Outdoor air monitoring in corridors with induced ventilation

We are currently working in a project where outdoor air requirements in corridors are met by means of induced ventilation (exhaust fans in contiguous WC's induce make-up air in the corridors). In this case is it necessary to install airflow monitoring devices in the exhaust fans of the WC's? Thanks in advance.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 01/24/2017 - 13:44

That would work, however it would likely be very expensive. You could also try to comply with the LEED CIR that allows motor current detection on systems that are constant volume.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.