FAQs about EAp2 :

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

Outdoor Air Intake: Baseline vs. Proposed

We are currently working on a LEED project whose Baseline Building will have an HVAC system 5 installed. Taking into account that section G3.1.1 of ASHRAE 91.1-2007 states that “for systems 5, 6, 7, and 8, each floor shall be modeled with separate HVAC system” we have modeled the system accordingly. For each floor we have divisions with different ratios of outdoor air intake and to respect those ratios we need to set the system to operate for the critical division. Taking into account that there are divisions with 100% of outdoor air in almost every floor, then almost every systems are being modeled for 100% of outdoor air, which is causing a great increase in the heat consumption. The problem is that by doing the aforementioned, the outdoor air intake of the Baseline will not be the same as the Proposed, but, if we do not proceed like above mentioned (i.e., if we set the system for the minimum outdoor air intake) we’ll not be ensuring that every division has the outdoor air intake that it’s supposed to have. In your opinion what should we do to solve this problem? Thank you.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 11/12/2012 - 14:46

The OA must be identical in total in both models (unless there is DCV in the Proposed and not the Baseline). Hard to tell how you fix the problem without knowing more about how you are modeling it. You should be entering the amount of OA and not having the software calculate it. Also keep in mind that the Baseline systems do not actually have to function from a design perspective, just from an energy perspective.