My project team wants to add the M&V however we are facing physical constraints on adding digital meters for all the electro-mechanical systems.
Could we count on the logical measurement via the BMS system monitoring to performance instead of having real accurate measurement?
Thank you.
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5907 thumbs up
September 30, 2013 - 9:29 am
You are not required to have any submeters by the IPMVP.
Measurements from the BMS may work. Just be sure that the M&V Plan spells out how these will translate to a measurement of energy use for each of the major energy end uses.