EBOM-2009 IEQp1:Minimum indoor air quality performance

Option B Calculator

Where can I find the Option B Calculator that is used to calculate compliance with 10 CFM per person for AHU's unable to meet ASHRAE 62.1-2007?

1

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 01/25/2016 - 22:59

Hi Haley, there's no official calculator for this option. You can create your own spreadsheet listing out the following for each AHU complying via Case 2: - the number of occupants (system level) - the required outside air per Case 2 (e.g. occupants x 10 cfm) - the measured outside airflow This will let GBCI easily compare the required OA per Case 2 against the measured OA.