Option 1 Path 2 Temperature and Humidty Requirements

Path 1 indicates flush-out needs to be accomplished with 14,000 cu ft. of OA per sq. ft. of floor area while maintaining an internal temperature of at least 60 deg F and no more than 60% RH. However, as I'm reading through Path 2, there is no mention of maintaining a certain internal temperature or relative humidity. When I go to submit the temperature and humidity readings using Path 2 along with all the supporting documentation, will I be denied credit for this point if I have any out of range temperature and/or humidity points even though Path 2 does not temperature and humidity limitations? Thanks!

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 04/20/2016 - 16:31

The corrective action flush out is not specified to meet a pre-determined duration or temp/RH limit. I am not aware of any LEED Interpretation or CIR that sets precedence on this issue.

Fri, 04/22/2016 - 13:38

David, By corrective action flush-out, do you mean the "post-occupancy" flush-out? Thanks!

Fri, 04/22/2016 - 14:07

Corrective action flush-out must occur pre-occupancy. Resample and confirmation must also occur before occupancy.