Simple question but I do not see it addressed anywhere. We are planning to do the partial flush out during occupancy option. Once we have flushed with the required amount of air to allow initial occupancy, can we just run outside air 24/7 until we are done? It seems that this would be the best case scenario in providing occupant air quality during the flush out, but I wanted to be sure I wasn't missing something.
Thanks!
Gustavo De las Heras Izquierdo
LEED Expert181 thumbs up
August 6, 2021 - 5:44 pm
Hi Susan,
Yes, it is quite common to keep flushing outdoor air 24/7 untl you complete the volume required by the credit.