CI-2009 IEQc3.2:Construction IAQ management plan - before occupancy

Option 1 - Path 2

I just had a mechanical engineer point out that the partial flush-out option does not include the requirement to maintain 60 degree temperature and 60% humidity. It seems to me that this requirement would be the same for both flush-out paths, but it really does not say that. Does anyone know if the temp and humidity requirements should be included in this path?

1

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Sat, 07/28/2012 - 01:07

It does appear that your mechanical engineer has found a technicality. I would venture to guess that it is an oversight in the credit language and that the 60/60 rule was not specifically excluded in option 2. You'd likely be jeopardizing your chances of getting the credit if you don't make an effort to stay within the required ranges because the LEED review is likely to take the same stance. The ranges are there for a reason. Supplying low temperatures for a long period of time would be uncomfortable for people finishing up the construction (minor work usually continues after the construction and installation of all finishes is complete). Supplying air with high humidity could cause moisture build up and eventually mold - leading to poor IAQ.