I’m modeling a building that is connected to a district CHP system that produces heat and electricity.
No cooling system, neither in the building nor in the CHP system, is available. There is no back-up energy.
I’m using the document “Treatment of District or Campus Thermal Energy in LEED” and since detailed data concerning the CHP system are not available I’m using Option 1 (streamlined path).
The building is nonresidential and its surface is less than 2300m^2. For the baseline model shall I use system 3 or system 4 of table G3.1.1A? Because of Table 2 and Table 3 of “Treatment of District or Campus Thermal Energy in LEED”, I guess that I have to model "PSZ-AC w/distrct heating". Am I right?
What efficiencies shall I use (par. 2.4.1.2.3 and Appendix D regard Option 2 while I’m using Option 1)? I guess that I have to consider the purchased heat, not the primary energy, both for the model of the proposed building and for the baseline model, therefore efficiencies shall not be considered for heating. Am I right?
Regards
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium for
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5909 thumbs up
October 24, 2012 - 9:19 am
Assuming the ultimate heat source is fossil fuel (burned by the CHP) I would use system 3. Under Option 1 you are correct. Correct again on heating efficiency as the heat is just treated as purchased heat.
Francesco Passerini
engineer90 thumbs up
October 24, 2012 - 10:18 am
Thank you, Marcus.
In the CHP system the energy source is woodchip, but I think that if one uses Option 1 it doesn't matter what fuel is burned, because considering renewable energy used in the district CHP system in order to get points is possible only if Option 2 is used. Right?
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5909 thumbs up
October 24, 2012 - 10:26 am
Yes you are correct.